You can use the conversion_factor
parameter of the Transformer
class.
You can set a conversion factor for each input and each output flow.
Let’s assume that the efficiency of the process is 0.6. So you have to put 1.67 energy units into the process to get one energy unit of biogas. The input units are divided into 0.167 (10%) units electricity, 0.33 (20%) units heat and 1.17 (70%) units biomass. The model is using power and energy units only so you have to be sure that everything fits e.g. the temperature level and the energy content of the biomass.
from oemof.solph import (
Transformer,
Bus,
Flow,
EnergySystem,
Model,
Sink,
Source,
processing,
bel = Bus("bus electricity")
bbgas = Bus("bus biogas")
bbmas = Bus("bus biomass")
bheat = Bus("bus heat")
date_time_index = pd.date_range("1/1/2012", periods=3, freq="H")
es = EnergySystem(timeindex=date_time_index)
es.add(bel, bbgas, bbmas, bheat)
es.add(
Transformer(
label="biogas converter",
inputs={bel: Flow(), bbmas: Flow(), bheat: Flow()},
outputs={bbgas: Flow(variable_cost=5, nominal_value=34)},
conversion_factors={bheat: 0.2, bel: 0.1, bbmas: 0.7, bbgas: 0.6},
es.add(
Sink(
label="demand biogas",
inputs={bbgas: Flow(nominal_value=15, fix=[0.9, 0.3, 0.7])},
es.add(Source(label="electricity source", outputs={bel: Flow()}))
es.add(Source(label="biomass source", outputs={bbmas: Flow()}))
es.add(Source(label="heat source", outputs={bheat: Flow()}))
model = Model(es)
model.solve()
result = processing.results(model)
flows = pd.DataFrame(
"{0} to {1}".format(k[0].label, k[1].label): result[k]["sequences"][
"flow"
for k in result.keys()
if not isinstance(k[0], Source) and not isinstance(k[1], Sink)
print(flows.sum())
You get three i/o equations for your Transformer:
biogas/0.6 = heat/0.2
biogas/0.6 = electricity/0.1
biogas/0.6 = biomass/0.7
The biogas demand in the first time step is 15*0.9 = 13.5
heat = 13.5/0.6*0.2 = 4.5
electricity = 13.5/0.6*0.1 = 2.25
biomass = 13.5/0.6*0.7 = 15.75
Total input = 22.5
Check: 22.5*0.6 = 13.5